As a start, I would suggest getting a simple socket tester (Screwfix do one for £7.99). This looks like a plug with LEDs in it. You stick it in each socket and the lights and a buzzer tell you whether there are wiring faults, in particular whether there is an earth connection. But the whole thing sounds rather dubious. At the least you will need a new distribution board with RCDs, and plumbing should be bonded to the earth connection at the board (not the same as using the plumbing as the earth connection!).
its OK for a 2week sun spark , but a real spark will use a proper meter to tell him what the actual earth return path value is.
a "socket and see " will work with a return path of several hundred ohms , but for the device to work a 30A rewireable needs a return path of 0.95x2.64 ohms
if the proepr R1 +R2 test and then a measured EFLI gives values under that prescribed in BS7671 then the installation is still safe. there will be recomendations to improve with RCD and split boards to minimise nuisance in the event of a fault on one side but its not a you must .
NEW installations however have a huge amount of items that MUST be fitted. even with the steel conduit in the walls an RCD will be needed as it is a domestic install.