Basis of the Connection Offer
2.1 Customer’s Installation
2.1.1 WPD understands that, based on current information provided by the Customer, including
within the Customer’s connection application, the Customer's Installation will comprise the
following:-
Total installed 10kW PV with an export of 7kW PV.
2.2 Supply Specification for the Proposed Generation Equipment
2.2.1 The characteristics of the Customer’s Installation(s) will be:
Nominal Voltage at Connection Point: 230/400 Volts
No of Phases: 1
Nominal Frequency: 50 Hz
Maximum Export Capacity: 7kW
Maximum Import Capacity: 15kVA
External Earth Loop Impedance: Existing connection
Maximum Prospective Short Circuit Current: Existing connection
Acceptable Power Factor for Export Capacity: 0.98 lead to unity.
Acceptable Power Factor for Import Capacity: 0.95 lag to unity.